"Rick Merrill" <> schreef in bericht
news

l4kd.317569$wV.17210@attbi_s54...
> If a UPS (power supply) is rated "1200 VA" and "640 watts" is
> the efficiency 640/1200 and would it be expected to drive a 64 watt AC
> load for 10 hrs??? Thanks. - RM
VA is needed if Voltage and Current are not in phase.
You need the "watts", thats the energy.
Like Rick said, if 640 runs 5 minutes, you would expect 64 watt to run 50
minutes.
In he real world of UPS the amount of time will increase with around a
factor 2, so still not 10 hours.
Do the calculation the other way around:
64x10= 640W.
Efficiency is less then 50% so around 1.2kWH is needed.
If the internal batteries are 24 volt, you will need 50AH.
This means a very heavy UPS as most UPS's have around 12 or 20AH onboard.
Cheers,
Jack