First if I may give a brief background: despite having space in a data
centre with UPS, diesel generator etc etc our data centre supplier has
managed to have 3 power outages in 6 months (ironically none due to
mains power failure) and it has moved beyond ridiculous. We are
looking around alternatives, but in the mean-time I need to take
immediate action to assuage our own client's concerns.
To that end I plan to put a standard APC UPS unit into our rack. I'm
looking at the APC Smart-UPS XL Modular 3000VA 230V Rackmount
(
http://www.apc.com/resource/include/...UM3000RMXLI2U),
plus extra battery, from which we should get about 30 mins runtime.
This is what the APC selector tool suggests for our exact config.
However, here's the problem: we have a 10 amp feed to the rack. The
power bar currently shows from 4 amp to 6 amp draw depending on the
server load. The APC unit above has a 16 amp IEC-320 C20 input.
My question is: can I safely use this UPS because my equipment is not
going to be drawing the unit's maximum power? The lady I phoned at
APC hinted (without saying directly) that I should be fine but stuck
to the official line which was that I should upgrade the power feed to
16A for safety. Thing is that doing so will set us back a fair bit
each month, which doesn't sit comfortably given that I'm only having
to do this to fix what is the data centre's fault!
Hoping someone with electrical/UPS experience can confirm/deny this!
Many thanks,
Louis